Technical Booklet E Fire Safety·Page 99·Table 4.2
Minimum periods of fire resistance by building use and height
Table 4.2 specifies the minimum fire-resistance periods in minutes required for structural elements and building components based on the building's purpose group (use class), storey depth/height, and whether sprinkler systems are installed.
Table 4.2 NEW Minimum periods of fire resistance
Purpose group of building | Minimum period (minutes) for elements of structure and other components of the building forming part of
Basement storey+ including floor over | Ground or upper storey
Depth (m) of basement | Height (m) of top floor above ground in building or separated part of building (1)
More than 10 | Not more than 10 | Not more than 5 | More than 5 not more than 11 | More than 11 not more than 18 | More than 18 not more than 30 | More than 30
1 Residential (dwellings) –
(a) flats
(i) not sprinklered: 90 | Not relevant | 60 | 30* | 30* | 60(2)** | 60@
(ii) sprinklered(3): 90 | Not relevant | 30* | 30* | 60(2)** | 60@ | Not(4) Permitted
(b) and (c) dwellinghouses: 90 | Not relevant | 60 | 30* | 30* | 60** | 60@ | Not(4) Permitted | 90** | Not relevant | Not(4) Permitted | 120** | Not relevant
2 Residential –
(a) institutional(5): 90 | 60 | 30*## | 60 | 60 | 90 | 120#
(b) other residential(6): 90 | 60 | 30* | 60 | 60 | 90 | 120#
3 Office –
not sprinklered: 90 | 60 | 30* | 60 | 60 | 90 | Not permitted
ssprinklered(3): 60 | 60 | 30* | 30* | 30* | 60 | 120#
4 Shop and commercial –
not sprinklered: 90 | 60 | 60 | 60 | 60 | 90 | Not permitted
sprinklered(3): 60 | 60 | 30* | 60 | 60 | 60 | 120#
5 Assembly and recreation –
not sprinklered: 90 | 60 | 60 | 60 | 60 | 90 | Not permitted
sprinklered(3): 60 | 60 | 30* | 60 | 60 | 60 | 120#
6 Industrial –
not sprinklered: 120 | 90 | 60 | 90 | 90 | 120 | Not permitted
sprinklered(3): 90 | 60 | 30* | 60 | 60 | 90 | 120#
7 Storage and other non-residential –
(a) any building or part not described elsewhere –
not sprinklered: 120 | 90 | 60 | 90 | 90 | 120 | Not permitted
sprinklered(3): 90 | 60 | 30* | 60 | 60 | 90 | 120#
Source — /Users/richardhill/Documents/planning-arch-project/data/documents/regional/Technical Booklet E - Fire Safety.pdf