Technical Booklet E Fire Safety·Page 97·Table 4.2
Table 4.2 Minimum periods of fire resistance
Sets out the minimum fire resistance periods in minutes required for structural elements and building components, varying by building purpose group, basement depth, and height of top floor above ground.
Table 4.2 Minimum periods of fire resistance
Purpose group of building | Minimum period (minutes) for elements of structure and other components of the building forming part of:
Basement storey+ including floor over (Depth (m) of basement: More than 10 / Not more than 10) | Ground or upper storey (Height (m) of top floor above ground in building or separated part of building: Not more than 5 / More than 5 not more than 18 / More than 18 not more than 30 / More than 30)
1 Residential (dwellings) – (a) flats (b) and (c) dwellinghouses | 90 / Not relevant | 60 / 30* / 30* / 30* | 60(2)** / 60@ / 90** / Not relevant / 120** / Not relevant
2 Residential – (a) institutional (b) other residential | 90 / 90 | 60 / 60 | 30*## / 30* / 60 / 60 / 90 / 90 / 120# / 120#
3 Office – not sprinklered / sprinklered(3) | 90 / 60 | 60 / 60 | 30* / 30* / 60 / 30* / 90 / 60 / Not permitted / 120#
4 Shop and commercial – not sprinklered / sprinklered(3) | 90 / 60 | 60 / 60 | 60 / 30* / 60 / 60 / 90 / 60 / Not permitted / 120#
5 Assembly and recreation – not sprinklered / sprinklered(3) | 90 / 60 | 60 / 60 | 60 / 30* / 60 / 60 / 90 / 60 / Not permitted / 120#
6 Industrial – not sprinklered / sprinklered(3) | 120 / 90 | 90 / 60 | 60 / 30* / 90 / 60 / 120 / 90 / Not permitted / 120#
7 Storage and other non-residential – (a) any building or part not described elsewhere – not sprinklered / sprinklered(3) | 120 / 90 | 90 / 60 | 60 / 30* / 90 / 60 / 120 / 90 / Not permitted / 120#
Source — /Users/richardhill/Documents/planning-arch-project/data/documents/regional/Technical Booklet E - Fire Safety.pdf