Technical Booklet E Fire Safety·Page 95·Table 4.1
Fire Resistance Testing Requirements for Building Elements
Table 4.1 specifies minimum fire-resistance provisions for various building elements when tested to BS 476 or European standards, including loadbearing capacity, integrity, and insulation requirements measured in minutes.
Table 4.1 Specific provisions of test for fire resistance of elements of structure and other components of a building (cont'd)
Part of building | Minimum provisions when tested to the relevant part of BS 476 (minutes) | Minimum provisions when tested to the relevant European standard (minutes) | Method of exposure
15 Cavity barrier | Not applicable | 30 15 EI 30 | Each side separately
16 Ceiling shown in Diagram 4.6 or 4.7 | Not applicable | 30 30 EI 30 | From underside
17 Fire-resisting duct referred to in paragraph 4.42(e) | Not applicable | 30 No provision E 30 | From outside
18 Casing around a drainage system as shown in Diagram 4.11 | Not applicable | 30 No provision E 30 | From outside
19 Flue walls described in paragraph 4.45 | Not applicable | See Table 4.2 | See Table 4.2 | EI see Table 4.2 | From outside
20 Fire doors | See Table 4.5 | See Table 4.5