Technical Booklet E Fire Safety·Page 84·3.5
Classification of Thermoplastic Materials
Thermoplastic materials are classified into three types (TP(a) rigid, TP(a) flexible, and TP(b)) based on their softening point and fire performance when tested to specific British Standards.
The term thermoplastic material includes all synthetic polymeric materials which have a softening point lower than 200ºC when tested to BS EN ISO 306: Method A120 Plastics. For the purposes of this Section (and Section 4) thermoplastic materials are classified as TP(a) rigid and TP(a) flexible and TP(b) as follows –
(a) To be classified as TP(a) rigid, a thermoplastic material should be –
(i) rigid solid PVC sheet;
(ii) solid polycarbonate sheet not less than 3 mm thick;
(iii) double or multiple skin rigid sheet of unplasticised PVC or polycarbonate which achieves a classification of Class 1; or
(iv) a rigid product, a specimen of which (at the thickness of the product as put on the market) when tested to BS 2782-0: Method 508A, extinguishes before the flame reaches the first mark and after removal of the burner, the flaming or afterglow does not exceed 5 seconds.
(b) To be classified as TP(a) flexible, a thermoplastic material should be a flexible product not greater than 1 mm thick which complies with the Type C requirements of BS 5867: Part 2 when tested to BS 5438 Test 2 (excluding the cleansing procedure) with the flame applied to the surface of the specimens for 5, 15, 20 and 30 seconds respectively.
(c) To be classified as TP(b) a thermoplastic material should be –
(i) rigid solid polycarbonate sheet less than 3 mm thick;
(ii) double or multiple skin polycarbonate sheet which does not achieve a classification of Class 1; or
(iii) a product which, when a specimen of material between 1.5 mm and 3 mm thick, tested to BS 2782-0: Method 508A, has a rate of burning not greater than 50 mm per minute.
Source — /Users/richardhill/Documents/planning-arch-project/data/documents/regional/Technical Booklet E - Fire Safety.pdf