Technical Booklet E Fire Safety·Page 79·Table 2.9

Provisions for escape lighting by purpose group

Table 2.9 specifies which areas of buildings in different purpose groups must have escape lighting that activates if mains supply fails.

Table 2.9 Provisions for escape lighting Purpose Group 2: All common escape routes (including external escape routes) Purpose Groups 3, 4(2), 6 and 7(a): (a) Underground or windowless accommodation (b) Stairways in a central core or serving storey(s) more than 18 m above ground level (c) Internal corridors more than 30 m long (d) Open-plan areas more than 60 m2 Purpose Groups 4(3) and 7(b): All escape routes (including external escape routes) except in a shop of not more than three storeys, with no sales floor greater than 280 m2, provided that the shop is not a restaurant or bar Purpose Group 5: All escape routes (including external escape routes) and accommodation except for– (a) accommodation open on one side to view sport or entertainment during daylight hours; and (b) parts of school buildings with natural light and used only during normal school hours All purpose groups: (a) All toilet accommodation having a floor area more than 8 m2 (b) Windowless toilet accommodation having a floor area not more than 8 m2 (c) Electricity generator rooms (d) Switch room/battery room for emergency lighting system (e) Emergency control room