Technical Booklet E Fire Safety·Page 78·2.93
Construction of escape stairs – materials of limited combustibility
Escape stairs and landings must be constructed of materials of limited combustibility in non-dwellinghouses, except in specific circumstances including two to three storey Purpose Group 1(a) or 3 buildings, flats, and certain external stairs.
Other than in a dwellinghouse every escape stair and its associated landings should be constructed of materials of limited combustibility where –
(a) it is the only stair serving the building (or part of the building), unless the building is of two or three storeys and is of Purpose Group 1(a) or Purpose Group 3;
(b) it is within a basement storey, unless it is within a flat with more than one storey;
(c) the height to any storey which it serves is more than 18 m above ground or final exit level;
(d) it is a firefighting stairway (see Section 6); or
(e) it is external, except in the case of a stair that connects the final exit level with a floor or flat roof less than 6 m above or below final exit level.
Combustible materials may be added to the upper surface of these stairs except in the case of firefighting stairways.