Technical Booklet E Fire Safety·Page 67·2.72

Use of space within protected stairways

Protected stairways may only contain limited accommodation and services: sanitary facilities (not cloakrooms), lifts (with restrictions in single-stairway buildings), and in multi-stairway buildings only reception areas up to 10 m² or fire-resisting cupboards.

A protected stairway, other than a firefighting stairway (see Section 6), should not contain any accommodation or services other than – (a) sanitary accommodation or wash rooms provided that they are not used as a cloakroom; (b) a lift, provided that in a building (or part of a building) with a single escape stairway the lift motor room is over the lift shaft or outside the protected stairway; and (c) where it is not the only protected stairway in a building (or part of a building) – (i) a reception desk or enquiry office area having an area of not more than 10 m2 and located at ground or access level; or (ii) a cupboard formed by fire-resisting construction.