Technical Booklet E Fire Safety·Page 65·Table 2.7
Minimum stair width for phased evacuation
The minimum width of stairs used for phased evacuation must be determined from Table 2.7 based on the maximum number of people on the most heavily occupied storey.
The minimum width of a stair for phased evacuation should be that given in Table 2.7 for the appropriate maximum number of people on the most heavily occupied storey.
Table 2.7 Minimum width of escape stairs for phased evacuation
Maximum number of people in any storey(1) | Stair width(2) (mm)
100 | 1000
120 | 1100
130 | 1200
140 | 1300
150 | 1400
160 | 1500
170 | 1600
180 | 1700
190 | 1800
Notes:
(1) Where the number of people (P) on the most heavily occupied storey is more than 190, the minimum width of the escape stair (W mm) should be calculated from W = (P x 10) – 100.
(2) Where the stair serves a storey more than 30 m above ground level the width should not exceed 1400 mm [see paragraph 2.63(d)].