Technical Booklet E Fire Safety·Page 44·2.26
Installation of smoke alarms and heat alarms
Smoke alarms and heat alarms must be permanently wired to a regularly used lighting circuit or a separately fused dedicated circuit, and may operate at low voltage via a mains transformer.
Smoke alarms and heat alarms should be permanently wired to either –
(a) a regularly used lighting circuit; or
(b) a circuit which –
(i) is separately fused at the distribution board;
(ii) serves only smoke alarms and heat alarms; and
(iii) where a residual current device is used – is not connected to a residual current device which is also used by any other circuit.
Smoke alarms and heat alarms may operate at a low voltage via a mains transformer. The cable for the power supply to, and interconnection of, the smoke alarms need not have special fire-survival properties.