Technical Booklet E Fire Safety·Page 14·0.3
Means of escape for shopping complexes
Guidance for shopping complexes requires that shop units' escape design be compatible with the overall fire strategy, with reference to BS 9999 and BS 5588-10, which applies more restrictive provisions for shop units with only one exit.
Although the guidance in Section 2 may be readily applied to individual shops, shopping complexes present a different set of escape problems. The design of shop units within a shopping complex should be compatible with the fire strategy for the complex as a whole. A suitable approach is given in the relevant recommendations of BS 9999 BS 5588-10.
Note – BS 5588-10 applies more restrictive provisions to shop units with only one exit in covered shopping complexes.
Source — /Users/richardhill/Documents/planning-arch-project/data/documents/regional/Technical Booklet E - Fire Safety.pdf