Technical Booklet D Structure·Page 62·4C.6

Maximum imposed loads on roofs, floors and ceilings

Specifies the maximum imposed loads that should not be exceeded for roof, floor, and ceiling elements, with load values varying by element type and span.

The maximum imposed loads on each element of the building should not exceed those given in Table 4C.1. Table 4C.1 Simplified maximum imposed loads Element | Loading --- | --- Roof | distributed load of 1.5 kN/m2 for spans not greater than 6m, and 1.00 kN/m2 for spans greater than 6m but not greater than 12m Floors | distributed load of 2.0 kN/m2 Ceilings | distributed load of 0.25 kN/m2 together with a concentrated load of 0.9 kN

Source — /Users/richardhill/Documents/planning-arch-project/data/documents/regional/Technical Booklet D - Structure.pdf