Technical Booklet D Structure·Page 42·Table 4B.22

Table 4B.22: Maximum clear span of purlins supporting rafters

Design table providing maximum clear spans in metres for timber purlins of various sizes supporting rafters, for roof pitches between 22.5° and 30° with an imposed load of 0.75 kN/m² and timber strength class C24.

Table 4B.22 Maximum clear span of purlins supporting rafters (m); Roof pitch more than 22.5° but not more than 30°; Imposed load of 0.75 kN/m2; Timber strength class C24. Dead Load [kN/m2] excluding the self weight of the purlin. Purlin sizes include 47 x 150, 47 x 175, 47 x 200, 47 x 225, 63 x 125, 63 x 150, 63 x 175, 63 x 200, 63 x 225, 75 x 125, 75 x 150, 75 x 175, 75 x 200, 75 x 225, 2 x 47 x 200, 2 x 47 x 225, 2 x 47 x 250, 2 x 47 x 275, 2 x 47 x 300 (all in mm). Design spacing of purlins: 1500, 1800, 2100, 2400, 2700, 3000 mm. Dead load categories: Not more than 0.50, More than 0.50 but not more than 0.75, More than 0.75 but not more than 1.00 kN/m2. Table provides maximum clear spans in metres for each combination of purlin size, spacing, and dead load.

Source — /Users/richardhill/Documents/planning-arch-project/data/documents/regional/Technical Booklet D - Structure.pdf