Technical Booklet D Structure·Page 37·Table 4B.12
Table 4B.12: Maximum clear span of purlins supporting rafters
This table provides maximum clear spans in metres for timber purlins of various sizes supporting rafters on roofs pitched more than 15° but not more than 22.5°, with an imposed load of 0.75 kN/m² and timber strength class C16. Spans vary based on purlin size, design spacing, and dead load.
Table 4B.12 Maximum clear span of purlins supporting rafters (m); Roof pitch more than 15° but not more than 22.5°; Imposed load of 0.75 kN/m2; Timber strength class C16 C16. Dead Load [kN/m2] excluding the self weight of the purlin. Size of purlin (mm): 47 x 150, 47 x 175, 47 x 200, 47 x 225, 63 x 150, 63 x 175, 63 x 200, 63 x 225, 75 x 125, 75 x 150, 75 x 175, 75 x 200, 75 x 225, 2 x 47 x 200, 2 x 47 x 225, 2 x 47 x 250, 2 x 47 x 275, 2 x 47 x 300. Dead loads: Not more than 0.50, More than 0.50 but not more than 0.75, More than 0.75 but not more than 1.00 kN/m2. Design spacing of purlins: 1500, 1800, 2100, 2400, 2700, 3000 mm. Maximum clear spans provided in the table in metres.