Technical Booklet C Site Preparation and Resistance to Contaminants and Moisture·Page 28·6.4(c)

External Cavity Wall Moisture Management

For external cavity walls, the cavity must extend at least 225 mm below the lowest damp proof course, or a cavity tray with weep holes every 900 mm must be provided to manage water penetration and moisture transfer.

if the wall is an external cavity wall (see Diagram 6.2), the cavity should be taken down at least 225 mm below the level of the lowest damp proof course, or a cavity tray should be provided to deflect penetrating water towards the outer face so as to prevent precipitation passing into the inner leaf. Weep holes should be provided every 900 mm to assist in the transfer of moisture through the external leaf. A cavity tray may be used where a cavity wall is constructed directly off a raft foundation, ground beam or similar supporting structure and it is impractical to continue the cavity down 225 mm.