Technical Booklet C Site Preparation and Resistance to Contaminants and Moisture·Page 23·5.8
DPM placement and vapour control layer requirements
When a DPM is placed on the warm side of insulation, it acts as a vapour control layer to prevent interstitial condensation. If the DPM is below the insulation without a VCL, condensation may accumulate over time, though high-vapour-resistance insulation may reduce this risk.
Where the DPM is on the warm side of the insulation it will also act as a vapour control layer (VCL) and prevent interstitial condensation forming on any of the layers on the cold side of the insulation. Where the DPM is placed at a lower level than the insulation and no VCL is provided there is a risk of interstitial condensation which may accumulate year-on-year. However, with insulation of high vapour resistance, a vapour control layer may not be necessary but designers should use condensation software to determine if there is a risk of a year-on-year build up of interstitial condensation (see paragraph 8.2).