Amendments Booklet AMD 9 2025 (Booklets E R)·Page 35·Table 4.2 (Notes)
Notes to fire resistance table for car parks
Provides clarifications and footnotes regarding the application of fire resistance periods, including provisions for basement floors, compartment walls, steel element specifications, and height-related sprinkler requirements.
+ The floor over a basement (or if there is more than one basement, the floor over the topmost basement) should meet the provisions for the ground and upper storeys if that period is higher.
* Increased to a minimum of 60 minutes for compartment walls separating buildings.
$ Increased to a minimum of 30 minutes for elements protecting the means of escape.
# Reduced to 90 minutes for elements not forming part of the structural frame.
(7) Car parks which comply with paragraphs 4.49 and 4.50.
(8) For the purposes of this technical booklet the following types of steel elements are deemed to have satisfied the minimum period of fire resistance of 15 minutes when tested to the European test method –
(i) Beams supporting concrete floors, maximum A/V = 230 m-1 operating under full design load.
(ii) Free standing columns, maximum A/V = 180 m-1 operating under full design load.
(iii) Wind bracing and struts, maximum A/V = 210 m-1 operating under full design load.
Guidance is also available in BS EN 1993-1-2.