Amendments Booklet AMD 9 2025 (Booklets E R)·Page 21·6.21C
EAS System Independence from Other Systems
Evacuation alert systems must be independent and separate from fire alarm systems. No fire detectors or other devices should be connected to the EAS, and it should not be integrated with fire detection or alarm systems.
An evacuation alert system is not, and should not be confused with, a fire alarm system. The EAS should not be integrated with a fire detection and fire alarm system (or any other system), nor should any devices (such as fire detectors), other than evacuation alert devices, be connected to the EAS.