Amendments Booklet AMD 9 2025 (Booklets E R)·Page 19·Diagram 6.1B

Location of firefighting shafts: hose laying distances

Diagram showing required hose laying distances from fire main outlets to ensure adequate firefighting coverage, with distances of 60m for installations with sprinklers and 45m for those without sprinklers.

Diagram 6.1B Location of firefighting shafts: hose laying distances See para 6.3C With sprinklers: 60m hose laying distance Without sprinklers: 45m hose laying distance Floor plan within 60m hose laying distance from fire main outlet Floor plan within 45m hose laying distance from fire main outlet Hose reach F Fire main outlet in a firefighting shaft H Fire main outlet in a protected stairway. 60m Additional hose coverage required NOTES: 1. Hose laying distances should be measured from the firemain outlet along the route suitable for laying hose. If this route is not known, the distance should be taken at two-thirds of the direct distance. 2. The fire main outlet should be located according to paragraph 6.9.