Amendments Booklet AMD 9 2025 (Booklets E R)·Page 18·6.3C(a)
Location of firefighting shafts with sprinkler systems
In sprinklered buildings, firefighting shafts and protected stairways must be located so that every part of every storey is no more than 60 m from a fire main outlet in a firefighting shaft.
If the building is fitted throughout with a sprinkler system in accordance with Section 8, then sufficient fire-fighting shafts should be provided so that every part of every storey is no more than 60 m from a fire main outlet in a firefighting shaft (see Diagram 6.1B a and b).