Amendments Booklet AMD 9 2025 (Booklets E R)·Page 10·2.17
Roof Space Conversion to Habitable Room or Kitchen
Conversions of roof spaces to habitable rooms or kitchens require automatic fire detection and alarm systems in the new room, circulation spaces, and affected habitable rooms. Provisions depend on whether the existing building has two storeys and floor area/room count restrictions.
Where a roof space is to be converted to a habitable room or kitchen, an automatic fire detection and fire alarm in accordance with paragraphs 2.23 or 2.24 should be provided within the new habitable room or kitchen; the circulation spaces from the new room to the final exit; and to any habitable room or kitchen opening on to the circulation spaces leading from the new room to the final exit and either – (a) the relevant provisions of paragraph 2.4 to 2.15 should apply; or (b) where the existing dwellinghouse has two storeys the provisions in paragraphs 2.18 to 2.22 may be followed provided that the new storey does not – (i) exceed 50 m2 in floor area; or (ii) contain more than two habitable rooms. Note – The general provisions of this Section apply to any other roof space conversion which adds a new storey to an existing dwellinghouse.