Amendments Booklet AMD 7 2022 (Booklets B C E)·Page 17·5.4B

Cavity surfaces in external wall construction with masonry or concrete inner leaf

Surfaces facing into cavities in external walls with masonry or concrete inner leaves must meet provisions of Table 5.1A and cavity barrier requirements in Section 4, unless Regulation 23(2) applies.

In the case of an external wall construction of a building which, by virtue of paragraph 4.40(d) (external cladding system with a masonry or concrete inner leaf), is not subject to the provisions of Table 4.7, the surfaces which face into cavities should also meet the provisions of Table 5.1A, and provisions for cavity barriers in Section 4, but where Regulation 23(2) applies, that regulation prevails over guidance provided in Table 5.1A and Section 4.