Technical Booklet H Stairs Ramps Guarding and Protection from Impact·Page 27·3.17

Landing provision and dimensions

A landing must be provided at the top and bottom of every flight with a width not less than the stair width and a depth not less than the stair width (for private stairs) or 1200 mm clear of door swing (for common stairs in blocks of dwellings).

A landing should be provided at the top and bottom of every flight. The width of a landing should be not less than the width of the stair. The going of a landing should be not less than – (a) in a private stair, the width of the flight; and (b) in a common stair in a block of dwellings, 1200 mm clear of any door swing onto them. Part of a floor may be considered as a landing.