Roof member sizes for imposed loads
4B.9NI-wide·Technical Booklet D Structure
Tables 4B.11 to 4B.44 give the sizes of certain roof members for imposed loads of 0.75 kN/m2 and 1.00 kN/m2. The loading applicable at a particular site depends on the elevation of that site above sea
structuralroofApplicability criteria for pitched roof timber tables
4B.9NI-wide·Technical Booklet D Structure
The tables for the pitched roof timbers are only applicable to a building where no access is provided to the roof, other than that necessary for cleaning and maintenance, which has – (a) a roof area n
structuralroofSimplified imposed roof loads by altitude and zone
Table 4B.2NI-wide·Technical Booklet D Structure
Table 4B.2 Simplified imposed roof loads Altitude of site above sea level (m) | Zone A (kN/m2) | Zone B (kN/m2) from 0 to 100 | 0.75 | 0.75 more than 100 but not more than 150 | 0.75 | 0.75 more than
structuralroofRoof snow load zones map
Diagram 4B.2NI-wide·Technical Booklet D Structure
Diagram 4B.2 Simplified roof snow load map showing Zone A and Zone B distribution across Northern Ireland. Where the site straddles the boundary between Zone A and Zone B the worst loading case should
structuralroofTable 4B.20: Maximum clear span of purlins supporting rafters
Table 4B.20NI-wide·Technical Booklet D Structure
Table 4B.20 Maximum clear span of purlins supporting rafters (m); Roof pitch more than 22.5° but not more than 30°; Imposed load of 0.75 kN/m2; Timber strength class C16 C16 Dead Load [kN/m2] excludi
structuralroofTable 4B.19: Maximum clear span of rafters
Table 4B.19NI-wide·Technical Booklet D Structure
Table 4B.19 Maximum clear span of rafters (m); Roof pitch more than 22.5° but not more than 30°; Imposed load 0.75 kN/m2; Timber strength class C16 Dead Load [kN/m2] excluding the self weight of the
structuralroofMaximum clear span of purlins supporting rafters
Table 4B.26NI-wide·Technical Booklet D Structure
Table 4B.26 Maximum clear span of purlins supporting rafters (m); Roof pitch more than 22.5° but not more than 30°; Imposed load of 1.00 kN/m2; Timber strength class C24 Dead Load [kN/m2] excluding t
structuralroofMaximum clear span of rafters
Table 4B.25NI-wide·Technical Booklet D Structure
Table 4B.25 Maximum clear span of rafters (m); Roof pitch more than 22.5° but not more than 30°; Imposed load 1.00 kN/m2; Timber strength class C24 Dead Load [kN/m2] excluding the self weight of the
structuralroofTable 4B.28: Maximum clear span of purlins supporting rafters
Table 4B.28NI-wide·Technical Booklet D Structure
Table 4B.28 Maximum clear span of purlins supporting rafters (m); Roof pitch more than 30° but not more than 45°; Imposed load of 0.75 kN/m2; Timbers strength class C16 C16 Dead Load [kN/m2 ] excludi
structuralroofTable 4B.27: Maximum clear span of rafters
Table 4B.27NI-wide·Technical Booklet D Structure
Table 4B.27 Maximum clear span of rafters (m); Roof pitch more than 30° but not more than 45°; Imposed load 0.75 kN/m2; Timber strength class C16 C16 Dead Load [kN/m2 ] excluding the self weight of t
structuralroofTable 4B.29: Maximum clear span of rafters for roof pitch 30° to 45°
Table 4B.29NI-wide·Technical Booklet D Structure
Table 4B.29 Maximum clear span of rafters (m); Roof pitch more than 30° but not more than 45°; Imposed load 0.75 kN/m²; Timber strength class C24 C24 Dead Load [kN/m²] excluding the self weight of th
structuralroofTable 4B.30: Maximum clear span of purlins supporting rafters for roof pitch 30° to 45°
Table 4B.30NI-wide·Technical Booklet D Structure
Table 4B.30 Maximum clear span of purlins supporting rafters (m); Roof pitch more than 30° but not more than 45°; Imposed load of 0.75 kN/m²; Timber strength class C24 C24 Dead Load [kN/m²] excluding
structuralroofTable 4B.31: Maximum clear span of rafters for roof pitch 30–45°
Table 4B.31NI-wide·Technical Booklet D Structure
Table 4B.31 Maximum clear span of rafters (m); Roof pitch more than 30° but not more than 45°; Imposed load 1.00 kN/m²; Timbers strength class C16 C16 Dead Load [kN/m²] excluding the self weight of t
structuraltimberroofpitched-roofTable 4B.32: Maximum clear span of purlins supporting rafters for roof pitch 30–45°
Table 4B.32NI-wide·Technical Booklet D Structure
Table 4B.32 Maximum clear span of purlins supporting rafters (m); Roof pitch more than 30° but not more than 45°; Imposed load of 1.00 kN/m²; Timber strength class C16 C16 Dead Load [kN/m²] excluding
structuraltimberroofpitched-roofTable 4B.33: Maximum clear span of rafters for pitched roofs
Table 4B.33NI-wide·Technical Booklet D Structure
Table 4B.33 Maximum clear span of rafters (m); Roof pitch more than 30° but not more than 45°; Imposed load 1.00 kN/m2; Timber strength class C24 excluding the self weight of the rafter Not more than
structuraltimberroofpitched-roofTable 4B.32: Maximum clear span of purlins (pitched roofs)
Table 4B.32NI-wide·Technical Booklet D Structure
Table 4B.32 Maximum clear span of purlins (m); Roof pitch more than 30° but not more than 45°; Imposed load 1.00 kN/m2; Timber strength class C24 excluding the self weight of the purlin Not more than
structuraltimberroofpitched-roofTable 4B.34: Maximum clear span of purlins supporting rafters
Table 4B.34NI-wide·Technical Booklet D Structure
Table 4B.34 Maximum clear span of purlins supporting rafters (m); Roof pitch more than 30° but not more than 45°; Imposed load of 1.00 kN/m2; Timbers strength class C24
structuraltimberroofpitched-roofMaximum clear span of flat roof joists for limited-access roofs
Table 4B.40NI-wide·Technical Booklet D Structure
Maximum clear span of flat roof joists (m); Access not limited to the purposes of cleaning and maintenance; Imposed load 1.50 kN/m2; Timber strength class C24 Table provides maximum clear spans for j
structuralnon-domesticdwellingtimberroofPurlins supporting decking or sheeting - span tables and design parameters
4B.15NI-wide·Technical Booklet D Structure
Tables 4B.41 to 4B.44 give the maximum clear span of purlins supporting decking or sheeting on roofs that have a pitch greater than 10o but not greater than 35o. The timber strength class used in the
structuralroofPurlin design loads and installation requirements
4B.15NI-wide·Technical Booklet D Structure
The tabulated purlin sizes are designed to resist only the load component perpendicular to the roof pitch with purlins installed normal to the roof pitch. Designers should ensure that the roof constru
structuralroofPurlin bearing and spacing details
4B.15NI-wide·Technical Booklet D Structure
clear span of purlin taken as the clear dimension measured horizontally between supports the minimum purlin bearing length should be 50 mm design spacing of purlins = (A + B)/2
structuralroofMaximum clear span of purlins supporting decking or sheeting (C16 timber) – Roof pitch more than 10° but not more than 35°
Table 4B.43NI-wide·Technical Booklet D Structure
Table 4B.43 Maximum clear span of purlins supporting decking or sheeting (m); Roof pitch more than 10° but not more than 35°; Imposed load of 1.00 kN/m2; Timber strength class C16 C16 Dead Load [kN/m
structuralroofMaximum clear span of purlins supporting decking or sheeting (C24 timber) – Roof pitch more than 10° but not more than 35°
Table 4B.44NI-wide·Technical Booklet D Structure
Table 4B.44 Maximum clear span of purlins supporting decking or sheeting; Roof pitch more than 10° but not more than 35°; Imposed load of 1.00 kN/m2; Timber strength class C24 C24 Dead Load [kN/m2] e
structuralroofGable wall strapping to roof
4C.25NI-wide·Technical Booklet D Structure
The gable wall should be strapped to the roof as shown in Diagram 4C.13(a) and (b) by tension straps as described in paragraph 4C.23. Vertical strapping at least 1 m long having a minimum cross-sectio
structuralwind-resistanceroof